A. Location
There must be at least one telecommunications equipment room (T-E-R) in a single-story building. For multi-story buildings, one T-E-R on the first floor (or basement) is required and at least one smaller telecommunications room (TR) is required on each floor above. T-E-Rs and TRs must be designed so that they are within 295 "cable feet" (90 meters) of every telecommunications outlet (TO) on that floor. If this is not possible then more than one TR per floor is required. (295 cable feet includes cable lengths through vertical walls, conduits, cable trays and other pathways between the patch panels in the TR and the TO.)
The best location for T-E-Rs or TRs is the building core. The rooms should be vertically aligned or stacked. They must be accessible either from the building exterior, public hallway or other common areas. They must not be located inside office spaces, class rooms or auditoria.
T-E-Rs and TRs must be dedicated to telecommunications. They may not contain electrical and mechanical equipment; fire alarm panels, slop sinks for janitors, etc. Equipment not related to the T-E-R and TR such as piping, duct work, building column and distribution of building power must not be located in or pass through the T-E-R or TRs.
B. Size
The size of the telecommunications spaces depends on the function and total area served. (Please refer to the sizing method for each specific type of telecommunications space in items K and L.)
C. Doors
The doors to the telecommunications rooms must open 180 degrees outward unless restricted by building code. They must be a minimum of 36" wide and 80" high with no door sills. For security reasons, doors must be equipped with locks. Locks must be keyed to UCSD standard utility room key (10544 or DB32 if the room is a telecommunications node room). This key assignment must be included in the keying schedule. Telecommunications rooms must not have windows.
D. Floors
Carpet is not permitted in any telecommunications spaces. Floors-- also walls and ceilings-- should be treated and sealed to eliminate dust. Static-controlled vinyl tiles are the preferred floor cover.
The rating for distributed floor loading for telecommunications room must be greater than 100 lbs/sq. ft. Concentrated loading must be greater than 2000 lbs in areas that will support telecommunications equipment.
E. Walls
All walls must be lined with ¾" void free A-C grade (or better) plywood. The plywood must be fire retardant or treated with at least two coats of fire retardant paint on all sides. Use light colored paint to aid with lighting in the rooms. The bottom of the plywood should be mounted 6" above finished floor (AFF). No electrical conduits, junction boxes or any other equipment may be mounted on or across any backboard.
F. Ceiling
Drop ceiling or suspended ceiling is not permitted in all telecommunications spaces. The minimum acceptable ceiling height is 8.5'. It should be unobstructed to provide space over the equipment racks for suspended cable trays or horizontal ladder racks. Sprinkler heads must be provided with cages to prevent accidental operations. Drainage troughs must be provided under the sprinkler pipes to prevent leakage onto the equipment. They must be as high as possible to avoid accidental operation from cable pulling activities.
G. Electrical Power
A minimum of two dedicated non-switched 3-wire120 volt A/C quad outlets are required for equipment power; each one on a separate branch circuit. Branch circuits for equipment power shall be protected and wired for 20A capacity. The outlets should be mounted 12 inches from the finished floor. Separate duplex convenience outlets shall be installed at 6-foot interval around the room. Emergency power should be utilized whenever possible. If there is a UPS and/or a generator in the building then the TRs should be connected to it.
H. Lighting
Lighting must have uniform intensity of 50 foot candles when measured 3 feet from the finished floor. Indirect lighting is not permitted. Lighting fixtures must be on separate electrical circuits separate from the circuit the feeds the electrical outlets in the room. Do not place light fixture above equipment racks, cabinets, frames or other freestanding equipment to avoid blocking of light.
I. Environmental Control
The temperature inside telecommunications rooms must be maintained between 64 ºF-75 ºF and relative humidity between 30%-55%. There must be at least one air exchange per hour in the rooms to maintain positive pressure inside the rooms.
J. Grounding
Per NEC and ANSI/EIA/TIA- 607 requirements, the telecommunications grounding and bonding infrastructure shall be designed and routed through each telecommunications space. Each telecommunications room shall be equipped with a Telecommunications Grounding Busbar (TGB) bonded directly to the Telecommunications Bonding Backbone (TBB). The busbars shall be a minimum of 6" in length, 2" in width and 1/4 thick. They shall be drilled and tapped to accommodate standard NEMA compliant grounding hardware. The TBB shall be a minimum of #6 AWG stranded copper grounding conductor and should be in conduits. All TBBs must be tied to the telecommunications main grounding busbar (TMGB) located in the equipment room (or main telecommunications room). The TMGB must be bonded to the building system ground with a minimum of 3/0 AWG stranded copper bonding conductor (BC). The ohmic resistance to ground from any point in the telecommunications grounding system must not be more than 3 ohms.
K. Telecommunications Equipment Room (T-E-R)
A telecommunications equipment room (T-E-R) is where the entrance conduits terminate. It is usually located on the ground floor but may also be located in the basement. A T-E-R typically functions as the main cross-connect (MCC). It is the main telecommunications serving point for the building. It will contain telecommunications equipment, much of it mounted on 19" racks. Cables will be spliced and terminated on the walls. It is important that the entrance conduits stub up in the T-E-R as close to a corner as possible.
Typical T-E-R dimensions are 12' x 12-1/2' (minimum) for a building serving fewer than 200 work areas --a typical work area (WA) is 10'x10' or 100 sq. ft. A larger building will require a larger T-E-R.
In certain buildings, the T-E-R will be further designated as a Node Room. A Node Room is used as a cabling hub not just for that building but for other buildings in that neighborhood of the campus. A Node Room requires additional space, air conditioning, and additional entrance conduits. It may require 30 amp outlets. In some cases, where a Node Rooms is designated in a building, a separate TR on the same floor as the Node Room may be required.
ACT will advise FD&C and the architect in the initial planning stage if a Node Room has been designated. No water sprinklers may be installed in a Node Room. A separate fire suppression system, based on one of the approved replacements for Halon, must be installed in coordination with the campus Fire Marshall.
A Node Room will house PBX telephone switching equipment, large wet- or dry-cell batteries, routers for campus wide area network (WAN), related local area network (LAN) switches, optical fiber cross connects and optical communications gear. Hence, it should be located so that it is accessible for the delivery of large equipment throughout its useful life. It must be at least 10' from a potential source of EMI (motors, transformers, photocopying equipment and the like).
L. Telecommunications Rooms (TRs)
TRs are smaller than T-E-Rs. They are the cabling hubs for floors within a building. They also contain network electronics, typically mounted in 19" racks.
- A TR serving 50 WAs or 5000 sq. ft. must be at least 10'x 8' in size. (A typical WA is 10'X10' or 100 sq. ft.)
- A TR serving an area larger than 5000 sq. ft. and less than or equal to 8000 sq. ft. must be at least 10'x 9'.
- A TR serving an area larger than 8000 sq. ft. and less than or equal to 10,000 sq. ft. must be at least 10'x 11'.
- For a building where useable floor area served is much less than 5000 sq. ft., a small 8'x 6' TR is adequate.
- A minimum of four 4-inch vertical riser conduits or sleeves are required between TRs. They must be installed as close to a corner in the TR as much as possible.